Pumping Prescriptions
Pumping Machinery LLC.
02/16/2017
Third in a Series
Editor’s Note: Barry T. Brown of Spurlock Station, Unit 2, East Kentucky Power Cooperative contributed to this column.
In the first two articles of this series (Pumps & Systems, December 2016, read it here, and January 2017, read it here), we discussed the issue of leaky seals on double-suction horizontal split-case pumps mounted in a (somewhat unusual) vertical orientation. Both sides (inboard and outboard) leaked on all three pumps for years in the specific power-generation unit at the East Kentucky Power site.
The earlier articles described the application of the PREMS-2A data acquisition system to initiate the troubleshooting process and evaluate the impact of operation (proximity to the best efficiency point [BEP]), vibrations (possible hammering effect on seals) and similar factors.
It was determined the pumps operated within satisfactory proximity to the BEP, and a continual monitoring of vibrations (including spectral analysis) revealed no issues.
The effect of the alignment and nozzle loads, as well as seal assembly detail, was to be evaluated next during the removal of a pump at the next outage. This article describes some findings of the pump removal and disassembly inspection.
.jpg)

- No radial runout issues on the shaft (before removing the rotor from the casing). Checked at the coupling end, between drive end (DE) bearing and seal and between non-drive end (NDE) bearing and seal.
- Axial end play of the shaft was essentially zero.
- No significant impeller runout.
- Minor wear of wear rings, with diametral clearance about 0.010 inches.
- Both sides of the impeller had some cavitation damage (after about seven years in service), although the NDE side had significantly more damage than the DE, indicating possible non-uniform suction piping flow.

.jpg)

.jpg)
- Verify proper fit between the elastomer and the shaft and determine the cause of excessive interference.
- Provide proper venting to eliminate air pocket at the seal area during startup.
- Use hard-to-hard seal configuration to resist any particulate that might enter with cooling water.
- Rebuild the pump with these modifications and monitor its performance.
Reader Input
Among the input we received from readers on the first two articles in this series, we would like to share some information on similar issues with seals from Lawrence Leising, maintenance supervisor for the Town Of Amherst, New York, Engineering Department’s Wastewater Treatment Division. “In your recent article—Case Study (part 1 of 3, read it here)—you referenced that the pumps were installed in a vertical position. We have vertical pumps with (single split) mechanical seals installed. We encountered a problem of short seal life as well, and I would like to pass on a solution which cured our problem. “In our vertical pumps we have a volute case air bleed valve that is opened to release air after a rebuild or for any dry pump startup. The seal also has a vent port into which a vent air release valve is installed. They are also flush/vent single seals. Typically the seal vent would be used to vent the seal before startup. “Our flush water has entrained air and so does the fluid being pumped. Due to the seal being at the pumps’ wet end high point, this is where the air collects—the flush water can’t displace it. “I happened to be looking at our hot water heating system in the plant one day and noticed the high vents installed to release air. This gave me the idea that because the high vent continuously releases air, it may be a good fit for the pump seals. We attached the air release valve to the pump frame higher than the seal. Flexible tubing connects the seal vent port to the valve. The valve uses an internal float and needle valve. Any trapped air is automatically released keeping the seal full of flush water. “Since doing this modification, our seal failure problem has been drastically reduced. The needle valve stays dry and clean because the float prevents water from getting to that point. Our seals are Chesterton 442s and the air release valve is made by ITT. We had a visit from a Chesterton field representative, he was amazed at our solution.”
To read more Pumping Prescriptions columns, click here.