A site visit and testing are critical to the process.
ProPump Services LLC

The Environmental Protection Agency’s (EPA) 316b requires utilities to reduce condenser cooling water velocity at intake screens to mitigate the impact on aquatic life. For utilities, this affects primarily “once-through” circulating water systems, or units without cooling towers. For existing plants, there is considerable flexibility on a local basis to support practical and cost-effective solutions to strike a balance between environmental and plant economic issues.

Image 1. Typical circulating water pump installationImage 1. Typical circulating water pump installation (Images courtesy of ProPump)

Compliance with EPA 316b can involve many solutions, including:

  • Modify circulating water pump design or operations: Throttling pumps (see Image 1), running fewer pumps, rerating one or more pumps
  • Incorporate variable speed drives (VSDs).
  • Increase inlet screen area (see Image 2).
  • Add a cooling tower.
  • Combinations of the above solutions
Image 2. Existing traveling screensImage 2. Existing traveling screens

Options should be evaluated for best fit based on 316b compliance, first cost, ongoing costs, time to implement and impact on unit capacity and heat rate.

As a cost-effective option, some plants have considered throttling their circulating pumps as a means to lower screen velocity. But simply reducing flow rate by throttling, if achievable, results in other trade-offs. While throttling is cost effective to try (and is reversible), it must be evaluated for impact on unit heat rate and output. Using the pump discharge valves or condenser inlet or outlet valves to throttle also requires review of the valve design for throttling mode. These valves are usually butterfly isolation type and not designed for continuous throttling. Additionally, the circulating water pumps may not be candidates for long term operation at the lower flow rates due to their particular hydraulic design.

Partial throttling (i.e. more modest flow reduction, staying above the recommended minimum flow rate) may be more practical if combined with other options, such as cascading pumps (idling one in the winter) or traveling screen inlet area increase. Several sites with older, idle units have been studied. These idle units could allow refurbishment and utilization of their existing intake structures to increase screen area and lower intake velocities without the major expense of new screens or intake structures.

Image 3. Dip the head-capacity curve for low head pumpsImage 3. “Dip” the head-capacity curve for low head pumps

From a pump hydraulic design perspective, once-through systems are high capacity, low head (low pressure) designs using high specific speed impellers (similar to boat propellers). High specific speed pump designs often have a dip or instability in the head-capacity curve at about half of full capacity (see Image 3). This is an area of hydraulic flow mismatch resulting in increased vibration and noise. This instability is generally to be avoided, and as a result, high specific speed pumps may have higher recommended minimum flow rates, up to 65 to 85 percent of design capacity. (Hydraulic Institute suggests 80 percent for specific speeds above 4,500.)

There are other factors that affect the acceptable minimum flow, such as impeller inlet velocity (tip speed), energy level, inlet design and materials of construction that also need to be considered. In general, lower energy pumps will operate acceptably at lower flow rates than higher energy pumps. One measure of energy level is the impeller tip speed, which is the velocity of the impeller inlet tip, typically expressed in feet per second. The inlet tip speed is calculated as shown in Equation 1.

Equation 1

Typical inlet tip speed design values for circulating water pumps range from 50 to 85 feet per second (ft/sec), with the higher tip speeds requiring higher minimum flow rates to avoid damage. Any consideration of throttling for long periods needs to evaluate the inlet tip speed as well as other key factors. From involvement in various 316b system studies, some generalizations can be made.

Circulating Water Pumps

Many older systems lack “design basis” documents, such as pump curves, system resistance curves and hydraulic gradients. These are important for analysis and future plant needs and can be recreated as part of the testing program if missing. Most pumps were not designed for low flow operation (some performance curves do not even provide low capacity data, since it is not recommended to run the pumps there). Many pump curves are not completely accurate due to worn pump components, inaccurate original curve (often the dip area is misrepresented), or use of incorrect replacement hydraulic components.

Circulating pumps used in parallel (most cases) must maintain the same rpm. If the system uses VSDs, they must be used on all pumps in a common unit and operate at nominally the same speed.

Cooling Water System

Condensers are often running inefficiently and lack instrumentation to monitor and trend performance including cleanliness (increased pressure drop due to tube fouling), liquid level in water boxes and presence of vacuum leaks.

Image 4. Wetted vibration transducersImage 4. Wetted vibration transducers provide vibration data below grade

Once-through systems have system resistance curves where the head varies with the square of capacity. This makes them a good fit for variable speed drives, since the pump head-capacity varies similarly—the pump remains at good efficiency and above minimum flow at all speeds (see Image 4). Reduced pump speed is usually obtained via variable frequency input to the motor but can also be obtained with a fluid or magnetic drive or a multi-speed motor.

Some units have low capacity factors, and may be cost constrained from major capital investments. The choice is to keep the costs modest or shut down the unit.

Instrumentation

Flow metering can be difficult on once-through systems due to buried pipe, pipe materials (concrete or concrete lined) and lack of accessibility. Several intrusive and non-intrusive methods can be employed to provide adequate flow metering results.

Circulating pump systems have minimal instrumentation, often lacking basis data such as:

  • discharge pressure
  • intake water level
  • vibration monitoring
  • motor amps
  • motor thrust bearing temperature

Vibration data below grade (wetted transducers) should be considered to improve the ability to monitor circulating water pump health and provide early indications of distress (see Image 6). Plants need a reliable method of estimating and reporting water usage to the regulatory agencies. This can be determined by direct measurement of velocity or calculated from other data. Due to the potential large expenditures for some of the possible options, it is beneficial to start with a system analysis to evaluate the original design, current operations and options for desired performance.

Analysis of the circulating water system involves multiple disciplines and includes the pumps, motors, condenser, valves, piping and ancillaries. An investigative process that has been successfully used at various locations includes the five key steps listed here.

Image 5. Site walkdown and data collectionImage 5. Site walkdown and data collection
  1. Visit the site and conduct a system walkdown. Collect data, drawings, curves, etc. Discuss plant goals and constraints (see Image 5).
  2. Develop a test plan. Discuss testing plan with site personnel.
  3. Perform system testing. Collect flow and pressures including pump discharge pressures, condenser inlet and outlet pressures, motor data. (There are many options for flow metering to determine existing pump and system performance. If possible, non-intrusive flow metering is performed. If this is impractical, there are alternate testing means to determine system capacity.)
  4. Perform an analysis of data and issue report and conclusions.
  5. Present options and cost/benefit analysis.

In conclusion, there are many options for compliance with 316b. Plants are different, and each one has a different set of constraints and cost/benefit situations. The lowest cost solution is typically to use existing hardware and modify operations to achieve compliance. If inadequate, various hardware changes can be made to pumps, motors (including VSDs), piping system, and/or intake screens to achieve compliance at an acceptable cost to the plant.